CHAPTER 5: SETTINGS FLEXLOGIC
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 5-209
5
GROUND IOC2 to 12 Same set of operands as shown for GROUND IOC 1
ELEMENT:
Ground time
overcurrent
GROUND TOC1 PKP
GROUND TOC1 OP
GROUND TOC1 DPO
Ground time overcurrent 1 has picked up
Ground time overcurrent 1 has operated
Ground time overcurrent 1 has dropped out
GROUND TOC2 to 6 Same set of operands as shown for GROUND TOC1
ELEMENT:
Incipient cable fault
detection
INCIPNT FLT 1 OP
INCIPNT FLT 1 OP A
INCIPNT FLT 1 OP B
INCIPNT FLT 1 OP C
INCIPNT FLT 1 PKP
INCIPNT FLT 1 PKP A
INCIPNT FLT 1 PKP B
INCIPNT FLT 1 PKP C
Asserted when incipient cable fault detector 1 operates in any phase
Asserted when incipient cable fault detector 1 operates in phase A
Asserted when incipient cable fault detector 1 operates in phase B
Asserted when incipient cable fault detector 1 operates in phase C
Asserted when incipient cable fault detector 1 picks up in any phase
Asserted when incipient cable fault detector 1 picks up in phase A
Asserted when incipient cable fault detector 1 picks up in phase B
Asserted when incipient cable fault detector 1 picks up in phase C
INCIPNT FLT 2 to 6 Same set of operands as shown for INCIPNT FLT 1
ELEMENT:
Non-volatile latches
LATCH 1 ON
LATCH 1 OFF
Non-volatile latch 1 is ON (Logic = 1)
Non-volatile latch 1 is OFF (Logic = 0)
LATCH 2 to 16 Same set of operands as shown for LATCH 1
ELEMENT:
Negative-sequence
instantaneous
overcurrent
NEG SEQ IOC1 PKP
NEG SEQ IOC1 OP
NEG SEQ IOC1 DPO
Negative-sequence instantaneous overcurrent 1 has picked up
Negative-sequence instantaneous overcurrent 1 has operated
Negative-sequence instantaneous overcurrent 1 has dropped out
NEG SEQ IOC2 Same set of operands as shown for NEG SEQ IOC1
ELEMENT:
Negative-sequence
time overcurrent
NEG SEQ TOC1 PKP
NEG SEQ TOC1 OP
NEG SEQ TOC1 DPO
Negative-sequence time overcurrent 1 has picked up
Negative-sequence time overcurrent 1 has operated
Negative-sequence time overcurrent 1 has dropped out
NEG SEQ TOC2 Same set of operands as shown for NEG SEQ TOC1
ELEMENT:
Neutral
instantaneous
overcurrent
NEUTRAL IOC1 PKP
NEUTRAL IOC1 OP
NEUTRAL IOC1 DPO
Neutral instantaneous overcurrent 1 has picked up
Neutral instantaneous overcurrent 1 has operated
Neutral instantaneous overcurrent 1 has dropped out
NEUTRAL IOC2 to 12 Same set of operands as shown for NEUTRAL IOC1
ELEMENT:
Neutral overvoltage
NEUTRAL OV1 PKP
NEUTRAL OV1 DPO
NEUTRAL OV1 OP
Neutral overvoltage element 1 has picked up
Neutral overvoltage element 1 has dropped out
Neutral overvoltage element 1 has operated
NEUTRAL OV2 to 3 Same set of operands as shown for NEUTRAL OV1
ELEMENT:
Neutral time
overcurrent
NEUTRAL TOC1 PKP
NEUTRAL TOC1 OP
NEUTRAL TOC1 DPO
Neutral time overcurrent 1 has picked up
Neutral time overcurrent 1 has operated
Neutral time overcurrent 1 has dropped out
NEUTRAL TOC2 to 6 Same set of operands as shown for NEUTRAL TOC1
ELEMENT:
PID regulator
PID 1 RAISE
PID 1 LOWER
PID 2 RAISE
PID 2 LOWER
PID 3 RAISE
PID 3 LOWER
PID 4 RAISE
PID 4 LOWER
ELEMENT:
Phase instantaneous
overcurrent
PHASE IOC1 PKP
PHASE IOC1 OP
PHASE IOC1 DPO
PHASE IOC1 PKP A
PHASE IOC1 PKP B
PHASE IOC1 PKP C
PHASE IOC1 OP A
PHASE IOC1 OP B
PHASE IOC1 OP C
PHASE IOC1 DPO A
PHASE IOC1 DPO B
PHASE IOC1 DPO C
At least one phase of phase instantaneous overcurrent 1 has picked up
At least one phase of phase instantaneous overcurrent 1 has operated
All phases of phase instantaneous overcurrent 1 have dropped out
Phase A of phase instantaneous overcurrent 1 has picked up
Phase B of phase instantaneous overcurrent 1 has picked up
Phase C of phase instantaneous overcurrent 1 has picked up
Phase A of phase instantaneous overcurrent 1 has operated
Phase B of phase instantaneous overcurrent 1 has operated
Phase C of phase instantaneous overcurrent 1 has operated
Phase A of phase instantaneous overcurrent 1 has dropped out
Phase B of phase instantaneous overcurrent 1 has dropped out
Phase C of phase instantaneous overcurrent 1 has dropped out
PHASE IOC2 to 12 Same set of operands as shown for PHASE IOC1
Operand type Operand syntax Operand description