CHAPTER 5: SETTINGS GROUPED ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 5-239
5
Figure 5-126: Neutral time overcurrent 1 logic
5.7.4.3 Neutral instantaneous overcurrent (ANSI 50N, IEC PIOC)
SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  NEUTRAL CURRENT  NEUTRAL IOC1(12)
The neutral instantaneous overcurrent element can be used as an instantaneous function with no intentional delay or as a
definite time function. The element essentially responds to the magnitude of a neutral current fundamental frequency
phasor calculated from the phase currents. A positive-sequence restraint is applied for better performance. A small portion
(6.25%) of the positive-sequence current magnitude is subtracted from the zero-sequence current magnitude when
forming the operating quantity of the element as follows:
I
op
= 3 x (|I_0| - K x |I_1|) where K = 1/16 Eq. 5-16
The positive-sequence restraint allows for more sensitive settings by counterbalancing spurious zero-sequence currents
resulting from:
System unbalances under heavy load conditions
Transformation errors of current transformers (CTs) during double-line and three-phase faults
Switch-off transients during double-line and three-phase faults
NEUTRAL IOC1
NEUTRAL IOC1
FUNCTION: Disabled
Range: Disabled, Enabled
NEUTRAL IOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
NEUTRAL IOC1
PICKUP: 1.000 pu
Range: 0.020 to 30.000 pu in steps of 0.001
NEUTRAL IOC1 PICKUP
DELAY: 0.00 s
Range: 0.00 to 600.00 s in steps of 0.01
NEUTRAL IOC1 RESET
DELAY: 0.00 s
Range: 0.00 to 600.00 s in steps of 0.01
NEUTRAL IOC1 BLOCK:
Off
Range: FlexLogic operand
NEUTRAL IOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
NEUTRAL IOC1
EVENTS: Disabled
Range: Disabled, Enabled

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals