EasyManua.ls Logo

GE F35

GE F35
682 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Loading...
5-252 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
GROUPED ELEMENTS CHAPTER 5: SETTINGS
5
Figure 5-135: Phase undervoltage1 logic
5.7.8.3 Phase overvoltage (ANSI 59P, IEC PTOV)
SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  VOLTAGE ELEMENTS  PHASE OVERVOLTAGE1
There are three phase overvoltage elements available. A phase overvoltage element is used as an instantaneous element
with no intentional time delay or as a definite time element. The input voltage is the phase-to-phase voltage, either
measured directly from delta-connected VTs or as calculated from phase-to-ground (wye) connected VTs. The figure
shows specific voltages to be used for each phase.
PHASE
OVERVOLTAGE1
PHASE OV1
FUNCTION: Disabled
Range: Disabled, Enabled
PHASE OV1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
PHASE OV1
PICKUP: 1.000 pu
Range: 0.004 to 3.000 pu in steps of 0.001
PHASE OV1 PICKUP
DELAY: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
PHASE OV1 RESET
DELAY: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
PHASE OV1 BLOCK:
Off
Range: FlexLogic Operand
PHASE OV1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
PHASE OV1
EVENTS: Disabled
Range: Disabled, Enabled

Table of Contents

Related product manuals