5-302 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CONTROL ELEMENTS CHAPTER 5: SETTINGS
5
Figure 5-167: Thermal overload protection logic
5.8.10.7 Broken conductor detection
SETTINGS  CONTROL ELEMENTS  MONITORING ELEMENTS  BROKEN CONDUCTOR 1(6)
The broken conductor function detects a transmission line broken conductor condition or a single-pole breaker
malfunction condition by checking the phase current input signals and the I_2 / I_1 ratio. The intent is to detect a single-
phase broken conductor only. As such, two-phase or three-phase broken conductors cannot be detected.
To distinguish between single-phase disappearance and system disturbance in all three phases (such as load change and
switching), the broken conductor element monitors the change in all three phase currents at the present instance and at
four cycles previous. It also monitors changes in the I_2 / I_1 ratio, I_1 minimum, and I_1 maximum.
BROKEN CONDUCTOR 1
BROKEN CONDUCTOR 1
FUNCTION: Disabled
Range: Disabled, Enabled
BROKEN CONDUCTOR 1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
BROKEN CONDUCTOR 1
I2/I1 RATIO: 20%
Range: 20.0% to 100.0% in steps of 0.1%
BROKEN CONDUCTOR 1
I1 MIN: 0.10 pu
Range: 0.05 to 1.00 pu in steps of 0.01
BROKEN CONDUCTOR 1
I1 MAX: 1.50 pu
Range: 0.05 to 5.00 pu in steps of 0.01
BROKEN CONDUCTOR 1
PKP DELAY: 20.000 s
Range: 0.000 to 65.535 s in steps of 0.001
BROKEN CONDCT 1 BLK:
Off
Range: FlexLogic operand
BROKEN CONDUCTOR 1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
BROKEN CONDUCTOR 1
EVENTS: Disabled
Range: Disabled, Enabled

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals