5-330 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TESTING CHAPTER 5: SETTINGS
5
While in Forcible test mode, the relay contact outputs can be pre-programmed to respond in the following ways:
If set to “Normal,” the contact output remains fully operational. It operates when its control operand is logic 1 and
resets when its control operand is logic 0.
If set to “Energized,” the output closes and remains closed while the operand selected by the
TEST MODE FORCING
setting is On, regardless of the status of the operand configured to control the output contact. While the selected
operand is Off, the output behaves as it does when in service.
If set to “De-energized,” the output opens and remains opened while the operand selected by the
TEST MODE FORCING
setting is On, regardless of the status of the operand configured to control the output contact. While the selected
operand is Off, the output behaves as it does when in service.
If set to “Freeze,” the output retains its position at the instant before the
TEST MODE FUNCTION was Forcible and the
operand selected by the
TEST MODE FORCING setting was On, regardless of later changes in the status of the operand
configured to control the output contact. While the selected operand is Off, the output behaves as it does when in
service.
On restart, the
TEST MODE FORCING setting and the force contact input and force contact output settings revert to
their default states.

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals