3-22 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
WIRING CHAPTER 3: INSTALLATION
3
3.3.6.1  Contact inputs
A dry contact has one side connected to terminal B3b. This is the positive 48 V DC voltage rail supplied by the power supply 
module. The other side of the dry contact is connected to the required contact input terminal. Each contact input group 
has its own common (negative) terminal that must be connected to the DC negative terminal (B3a) of the power supply 
module. When a dry contact closes, a current of 1 to 3 mA flows through the associated circuit.
A wet contact has one side connected to the positive terminal of an external DC power supply. The other side of this 
contact is connected to the required contact input terminal. If a wet contact is used, then the negative side of the external 
source must be connected to the relay common (negative) terminal of each contact group. The maximum external source 
voltage for this arrangement is 300 V DC.
The voltage threshold at which each group of four contact inputs detects a closed contact input is programmable as 
17 V DC for 24 V sources, 33 V DC for 48 V sources, 84 V DC for 110 to 125 V sources, and 166 V DC for 250 V sources.
Figure 3-19: Dry and wet contact input connections
There is no provision in the relay to detect a DC ground fault on 48 V DC control power external output. We recommend 
using an external DC supply.
3.3.6.2  General application considerations
Contacts outputs of protective relays, auxiliary contacts from breakers, disconnectors and other devices, are generally 
connected to contacts inputs of protective relays. In some situations, the contact outputs of some protective relays can 
have high impedance connected across it. When such a contact output is connected across a F35 contact input, it can 
spuriously operate the F35 input even when the output is open, if there is a substantial distributed capacitance 
(represented by C1) present in the wiring between the output and the F35 input and the debounce time setting in the F35 
relay is low enough. This false assertion of the contact input, when there is inadvertent ground present at the DC positive 
terminal, can be prevented by inserting a resistor across the F35 input.
The following figure shows a typical DC circuit, with battery ground detection, of contact input. The contact output has 
parallel impedance across it (represented by R1).
Where a tilde “~” symbol appears, substitute the slot position of the module.