3-36 F650 Digital Bay Controller GEK-106310AE
3.1 ENERVISTA 650 SETUP SOFTWARE INTERFACE 3 HUMAN INTERFACES. SETTINGS & ACTUAL VALUES
3
Figure 3–16: COMMUNICATION TROUBLESHOOTING SCREEN
• Calibration (Serial or Ethernet connection): Allows retrieving the unit calibration settings and storing them in a file (with
extension *.cal). For reading or storing the calibration settings in the relay go to "Communications>Calibration>Get
or Set calibration settings" and select the intended calibration file. The calibration retrieval process is necessary to
be performed before updating the unit operative system, when the operating system is updated all the data in the relay
is deleted, including the factory calibration settings. When only the firmware is updated (for versions higher than 1.50),
the calibration settings are automatically saved in the relay.
• Upgrade firmware version (Ethernet connection): Go to "Communications>Upgrade relay", this menu allows the
user to update the firmware version of the relay through Ethernet communication. Firmware is related to the relay
internal program, designed by GE Multilin, which performs the protection and control functions, and which is run by the
relay main microprocessor.
IMPORTANT NOTE:
READ CAREFULLY THE FLASH MEMORY UPDATE PROCEDURE DESCRIBED IN
SECTION “BOOT CODE AND FIRMWARE" AND CLOSE ALL THE RUNNING
APPLICATIONS BEFORE PERFORMING FIRMWARE AND OPERATIVE SYSTEM
UPDATING PROCESS
For firmware versions lower than 7.00, before updating firmware check that the firmware
version that is going to be updated match the operative system version of the relay.
Otherwise it is necessary to update the operative system before proceeding to update
the firmware. Other combinations of firmware and operative system different from the
listed in section 5 will not be operative
For previous version than 7.00 the operative system version is available in the logotype
main screen in HMI; it is the number between brackets in the first line, e.g. F650 1.70
(2.35). The operative system version is 2.35