GEK-113000AE F650 Digital Bay Controller 2-29
2 PRODUCT DESCRIPTION 2.5 TECHNICAL SPECIFICATIONS
2
2.5.6.6 IRIG-B INPUT
2.5.7 REAL TIME CLOCK
Note: For relay's versions previous to 7.00, when the relay's date and time is changed using any of the documented
methods (Modbus, IRIG-B, SNTP, Front Panel...) the relay acknowledges and updates the time instantly but it is not until
after nearly 3 minutes that it is permanently stored in the Real Time Clock’s NVRAM.
2.5.8 OUTPUTS
2.5.8.1 REMOTE OUTPUTS (IEC61850 GSSE/GOOSE)
Amplitude modulation: DC SHIFT = Demodulated input (no carrier)
Input Voltage: TTL
Input Burden: 1.5 mA
Input Impedance: 3.3 kOhm
Minimum Input Voltage: 2.4 V
Maximum Input Voltage:
± 24 V
Formats: B000 (*) B001, B002 and B003 (*)
(*) Signal combinations recognized in accordance with IRIG Standard 200-95
Isolation: 2 kV
Accuracy:
Typical ±20 ppm
Backup energy: More than 1 week
Single Contact Carry continuous: 16 A
Make and Carry for 1 sec. 60 A
Break at L/R of 40 ms: 0.3 A DC max. at 125 Vdc
0.25 A DC max. at 250 Vdc
Operate Time: < 8 ms
Contact material: Silver Alloy
Output Logic Type, Output Type and Pulse Output Time are selectable by setting for each output
Output Logic Type Positive / Negative
Output Type Normal / Pulse / Latch (Selectable by setting for each output)
Pulse Output Time 0 to 60000 ms in steps of 1 ms (applicable only to signals set as pulse type)
Separate operate and reset signal can be configured by any digital signal programmable through PLC
Contact Outputs (F31-F33, F34-F36) for
board type 2 (supervision) in slot F:
The current seal-in circuit is used for verifying the current condition in a circuit
during the time that the tripping contact remains closed. If the current in the
tripping circuit is maintained over 500 mA, the function is sealed independently of
the status of the function that caused the trip.
Standard output points 32
User output points 32

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC