6-22 F650 Digital Bay Controller GEK-113000AE
6.15 OVERVOLTAGE ELEMENTS (59P, 59X, 59NH, 59NL, 47) 6 COMMISSIONING
6
6.15.3 59NH AND 59NL ELEMENTS
Set the relay as follows
Apply voltage as indicated on the table under the overvoltage setting level and verify that the relay does not trip.
Verify that the relay trips for the set voltage (with an admissible error of 5%).
This element can also be tested by applying only phase voltages. For this purpose, it is necessary to set Auxiliary Voltage =
VX. In this condition, Vn voltage is calculated as a sum of the phase voltages.
GENERAL SETTINGS
Auxiliary Voltage VN
NEUTRAL OV HIGH/LOW (59NH/59NL)
Function ENABLED
Pickup Level 120 V
Trip Delay 2.00
Reset Delay 0.00
ELEMENTS INPUT PICKUP LEVEL
(VOLTS)
TRIP DELAY
(SECONDS)
APPLIED
VOLTAGE (V)
TRIPPING TIME (S)
EXPECTED ADMISSIBLE
59NH/59NL VX 120 2 114 NO TRIP NA
132 2 [1.9–2.1 ]
132 2 [1.9 – 2.1]

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC

Related product manuals