5-22 F650 Digital Bay Controller GEK-113000AE
5.2 FIRMWARE UPGRADE VERSION V7.00 OR HIGHER 5 BOOTCODE AND FIRMWARE UPGRADE
5
5.2FIRMWARE UPGRADE VERSION V7.00 OR HIGHER
5.2.1 INTRODUCTION
This section explains how to upgrade the F650 firmware code for version V7.00 or higher.
BOOT CODE RELEASE NOTES
It is mandatory to maintain version compatibility between firmware and boot code in the upgrade procedure, otherwise the
relay will not start after upgrading.
BEFORE PERFORMING THE UPGRADE PROCEDURE CHECK THAT BOOT AND FIRMWARE VERSION MATCH.
5.2.2 COMMUNICATION PARAMETERS
1. Ethernet Connection/Type - Firmware upgrade processes require Ethernet communications. It is strongly recommended
to use a direct connection between the PC and the relay using a Cross-Over RJ45 Ethernet cable, instead a direct
connection through a hub or switch.
2. Relay IP Address - It must be assigned a IP address to the relay in the Ethernet parameters via HMI at PRODUCT
SETUP>COMMUNICATION>ETHERNET>ETHERNET E, A or B menu or via Enervista 650 Setup at
SETPOINT>PRODUCT SETUP>COMMUNICATION SETTINGS>NETWORK (Ethernet) E, A or B as shown in the Table
below.
Table 5–2: ETHERNET PARAMETERS
3. Example of IP Address Configuration:
The IP address and other parameters already assigned in the process will be:
IP Address:192.168.37.177
Netmask:255.255.255.0
Gateway:192.168.37.10
Note: To assure that the configuration is correctly setup it is possible to perform a ping command from the PC.
Firmware Bootware Enervista
7.12 7.12 7.20
7.20 7.12 7.20
PRODUCT SETUP>COMMUNICATION SETTINGS >NETWORK (ETHERNET)
NAME EVALUE UNITS RANGE
IP Address Oct1 192 [0 : 255]
IP Address Oct2 168 [0 : 255]
IP Address Oct3 37 [0 : 255]
IP Address Oct4 177 [0 : 255]
Netmask Oct1 255 [0 : 255]
Netmask Oct2 255 [0 : 255]
Netmask Oct3 255 [0 : 255]
Netmask Oct4 0 [0 : 255]
PRODUCT SETUP>COMMUNICATION SETTINGS >ROUTING
NAME EVALUE UNITS RANGE
Default RT GWY Oct1 192 [0 : 255]
Default RT GWY Oct2 168 [0 : 255]
Default RT GWY Oct3 37 [0 : 255]
Default RT GWY Oct4 10 [0 : 255]