GEK-113000AE F650 Digital Bay Controller D-31
APPENDIX D D.2 FACTORY DEFAULT CONFIGURATION
D
D.2FACTORY DEFAULT CONFIGURATION
NOTE:
SOURCE COLUMN:
This columns allow selecting the simple or complex (OR signal or Virtual output) operand that actives the selected
elements on relay configuration
If more than one operands are selected, the relay performs an OR gate with them to activate the selected element.
SIGNAL LOGIC COLUMN:
Refers to each individual signal selected on its left. NOT legend means that the refered signal is inverted
SOURCE LOGIC COLUMN:
Refers to the whole SOURCE signal selected on its left. NOT legend means that SOURCE signal is inverted
If more than one operand were selected, the OR gate output is inverted
SETPOINT>RELAY CONFIGURATION>OUTPUTS
OUTPUT SOURCE SOURCE LOGIC LOGIC
CONT OP OPER_F_01 VO_000_PROTECTION_ALARM -
CONT OP OPER_F_02
VO_046_59P_PKP -
VO_045_27P_PKP -
CONT OP OPER_F_03 VO_048_50G_PKP -
CONT OP OPER_F_04 VO_049_51G_PKP -
CONT OP OPER_F_05
VO_051_50PH_PKP -
VO_050_50PL_PKP -
CONT OP OPER_F_06 VO_053_51P_PKP -
CONT OP OPER_F_07
OPERATION BIT 1 -
AR CLOSE BREAKER -
CONT OP OPER_F_08
OPERATION BIT 2 -
VO_083_GENERAL_TRIP -
SETPOINT>RELAY CONFIGURATION>LEDS
LED SOURCE SOURCE LOGIC LOGIC LED NAME
LED01 VO_000_PROTECTION ALARM - PROT ALARM
LED02 VO_083_GENERAL_TRIP - TRIP
LED03 VO_019_PHASE_OVERCURRENT_TRIP - 50/51P TRIP
LED04 VO_069_GROUND_OVERCURRENT_TRIP - 50/51G TRIP
LED05
VO_074_59P_TRIP
- - 27/59 TRIP
VO_073_27P_TRIP
LED06 VO_085_GENERAL_PKP - PICKUP
LED07 VO_007_PHASE_OVERCURRENT_PKP - 50/51P PICKUP
LED08 VO_009_GROUND_OVERCURRENT_PKP - 50/51G PICKUP
LED09 VO_045_27P_PKP - 27 PICKUP
LED10 VO_046_59P_PKP - 59 PICKUP
LED11 AR READY - 79 READY
LED12 AR RCL IN PROGRESS - 79 IN-PROG
LED13 AR BLOCK - 79 BLOCK
LED14 AR CONDS INPUT NOT 79 INHIBIT
LED15 AR LOCKOUT - 79 LOCKOUT
SETPOINT>RELAY CONFIGURATION>PROTECTION ELEMENTS
PROTECTION ELEMENT SOURCE SIGNAL LOGIC SOURCE LOGIC
LED RESET INPUT OPERATION BIT 3
CHANGE LOCAL-
REMOTE
Not Configured
CHANGE OP BLOCKED Not Configured