GEK-113000AE F650 Digital Bay Controller 1-11
1 GETTING STARTED 1.2 OVERVIEW
1
Figure 1–6: 650 CONCEPT BLOCK DIAGRAM
b) F650 SIGNAL TYPE
Contact Inputs/Outputs are digital signals.
CT and VT inputs: are signals coming from the inputs of current and voltage transformers, used for monitoring the power
system signals.
CAN Bus Inputs/Outputs: are signals associated to physical input/output contacts from independent modules connected to
the 650 unit via a CAN Bus.
PLC: Programmable Logic Controller. Control module that enables the unit configuration (assignment of inputs/outputs)
and the implementation of logic circuits.
Protection Elements: Relay protection elements, for example: Overcurrent, overvoltage, etc.
Remote inputs and outputs provide a means of sharing digital point state information between remote devices using IEC
61850 GSSE and GOOSE messages.
Analog Inputs are signals associated with transducers.

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC