GEK-113000AE F650 Digital Bay Controller 2-15
2 PRODUCT DESCRIPTION 2.5 TECHNICAL SPECIFICATIONS
2
2.5.1.19 AUXILIARY OVERVOLTAGE (59X)
2.5.1.20 AUXILIARY UNDERVOLTAGE (27X)
2.5.1.21 UNDERFREQUENCY (81U)
Voltage Input Fundamental Phasor of the auxiliary voltage
Pickup level 3 to 300 in steps of 1 V
Dropout level 97% to 98% of the pickup level
Level accuracy
±1% of reading from 10 to 208 V at nominal frequency
Trip delay 0.00 to 900.00 s. in steps of 0.01 s
Reset delay 0.00 to 900.00 s. in steps of 0.01 s
Timing accuracy ±3.5% of operate time or 50 ms. (whichever is greater)
Snapshot Events Selectable by setting
Voltage Input Fundamental Phasor of the auxiliary voltage
Pickup level 3 to 300 V in steps of 1 V
Dropout level 102% to 103% of the pickup level
Level accuracy
±1% of reading from 10 to 208 V at nominal frequency
Curve Shapes Fixed time or inverse curve
Reset type Instantaneous
Curve Multiplier (Time Dial) 0.00 to 900.00 s. in steps of 0.01 s
Timing accuracy ±3.5% of operate time or 50 ms. (whichever is greater)
Snapshot Events Selectable by setting
Pickup level 20.00 to 65.00 Hz in steps of 0.01 Hz
Dropout level Pickup + 0.03 Hz
Level accuracy
±0.05 Hz of the reading from 30 to 80 Hz
Trip delay 0.00 to 900.00 s. in steps of 0.01 s
Reset delay 0.00 to 900.00 s. in steps of 0.01 s
Minimum voltage threshold 10 to 300V in steps of 1 V
Time Delay Accuracy 0 to 7 cycles
Operate time Typically 10 cycles at 0.1Hz/s change
Snapshot Events Selectable by setting

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC

Related product manuals