2-18 F650 Digital Bay Controller GEK-113000AE
2.5 TECHNICAL SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
2.5.2.2 SYNCHROCHECK (25)
2.5.2.3 FUSE FAILURE
2.5.2.4 BREAKER FAILURE (50BF)
Dead/live levels for line and bus 0.00 to 300.00 in steps of 0.01 V
Maximum voltage difference 2.00 to 300.00 V in steps of 0.01 V
Maximum angle difference 2.0º to 80.0º in steps of 0.1º
Maximum frequency slip 10 to 5000 mHz in steps of 10 mHz
Synchronism time 0.01 to 1.00 s in steps of 0.01 s
Angle accuracy 3º
Dead Source function None
(DL-DB) Dead Line - Dead Bus
(LL-DB) Live Line-Dead Bus
(DL-LB) Dead Line – Live Bus
Snapshot Events Selectable by setting
Algorithm based on positive sequence of voltage and current
Activation by V
2
/V
1
ratio
Current Input Fundamental Phasor (without harmonics)
Rated current For connection to 1 or 5 A CTs.
Pickup level for supervision 0.05 to 160.00 A in steps of 0.01 A
Pickup level for high level 0.05 to 160.00 A in steps of 0.01 A
Pickup level for low level 0.05 to 160.00 A in steps of 0.01 A
Pickup level for internal arcing 0.05 to 160.00 A in steps of 0.01 A
Dropout level 97% to 98% of the pickup level
Level Accuracy
±0.5% of the reading ± 10 mA from 0.05 to 10 A
±1.5% of the reading for higher values.
Timing accuracy ±3.5% of operate time or 50 ms. (whichever is greater)
Snapshot Events Selectable by setting