2-22 F650 Digital Bay Controller GEK-113000AE
2.5 TECHNICAL SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
2.5.2.14 BREAKER MAINTENANCE
2.5.2.15 SWITCHGEAR
2.5.2.16 MAXIMUM NUMBER OF STARTS
2.5.2.17 DIGITAL COUNTERS
2.5.2.18 COLD LOAD PICKUP
KI
2
t Breaker Counters for Phases A, B, C 0.00 to 9999.99 in steps of 0.01 (kA)
2
s
Breaker Openings Counter 0 to 9999 in steps of 1
Breaker Closings Counter 0 to 9999 in steps of 1
Switchgear 1 to16 (configurable in “relay configuration” screen).
Snapshot Events Selectable by setting (for each switchgear in “system setup”)
Metering algorithm Fundamental
Tripping time accuracy ±250ms or 5% whichever is greater
Full load amps 0.5 to 10.0 A in steps of 0.1
Breaker supervision Selectable by setting
Min. Stop time 0.0 to 900.0 in steps of 0.1
Number of starts 0 to 10 in steps of 1
Time to restart 0 to 100 minutes in steps of 1
Reset Counter Selectable by setting
Snapshot events: Selectable by setting
Operate time <45ms at 50Hz, typically
FUNCTION Disabled, Enabled
Name Any 12 alphanumeric characters
Preset -2147483648, 0, +2147483647
COMPARE -2147483648, 0, +2147483647
Cold Outage time 1 -1000 in steps of 1min
Cold Blocking time 1-1000 in steps of 1s