3-22 F650 Digital Bay Controller GEK-106310AE
3.1 ENERVISTA 650 SETUP SOFTWARE INTERFACE 3 HUMAN INTERFACES. SETTINGS & ACTUAL VALUES
3
3.1.8.3   BREAKER
This section shows the settings related to the Breaker definition such as shown in the following table
Table 3.9:  GENERAL OVERVIEW OF BREAKER MENU
3.1.8.4   PROTECTION ELEMENTS
This option shows all the protection-grouped elements available in the relay as shown in Table 3.10: or Table 3.11: (depend 
on firmware version). Each of these groups includes the specific protection units of the same type. For example phase 
currents group includes TOC, IOC, directional units, etc. There are three groups available, so there are three protection 
units of each function that can work in grouped mode or ungrouped (altogether). Users should take into account that 
position of different Enervista 650 PC Menus could vary depending on relay firmware version.
Table 3.10:  GENERAL OVERVIEW OF PROTECTION ELEMENTS MENU FOR FIRMWARE VERSION BELOW 7.50
Options enabled only in On-line mode are marked as (*). Options enabled only in Off-line mode are marked as (**)
Table 3.11:  GENERAL OVERVIEW OF PROTECTION ELEMENTS MENU FOR FIRMWARE VERSION 7.50 OR ABOVE
Options enabled only in On-line mode are marked as (*). Options enabled only in Off-line mode are marked as (**)
Breaker settings
Breaker settings, maintenance and switchgear selection of the device 
configured as breaker in the F650. The selected switchgear will be used 
in recloser, breaker failure and synchronism functions. The settings are 
Number of Switchgear, Maximum KI2t, KI2t Integ. Time, Maximum 
Openings, Max.Openings 1 hour and Snapshot Events.
Breaker maintenance
These settings correspond to the initialization of (KI)
2
t counters, and the 
counting of number of openings and closings of the switchgear 
configured as breaker. These Counters allow the breaker Maintenance. 
They are used to cumulate the breaker ageing produced by a trip or a 
breaker opening. In order to incorporate the breaker historic, in case of 
existing breakers, the system allows assigning an initial value to 
accumulated amperes, and to the number of opening and closing 
operations.
PROTECTION 
ELEMENTS
Phase Current All overcurrent grouped functions for phase current.
Neutral Current
All overcurrent grouped functions for neutral current. (Calculated from 
phases, not measured)
Ground Current
All overcurrent grouped functions for ground current. (Measured from 4th 
current input)
Sensitive Ground 
Current
All overcurrent grouped functions for sensitive ground current. 
(Measured from 5th current input)
Negative Sequence 
Current
All Negative sequence overcurrent grouped functions.
Voltage Elements
All voltage grouped functions for phases, neutral, ground and auxiliary 
voltage
Power
Forward power, directional power and wattmetric ground fault (High and 
Low) grouped protection functions.
PROTECTION 
ELEMENTS
Setting Groups 1
All protection functions that could be available when setting group 1 the 
active group
Setting Groups 2
All protection functions that could be available when setting group 2 the 
active group
Setting Groups 3
All protection functions that could be available when setting group 3 the 
active group
Setting Groups 4
All protection functions that could be available when setting group 4 the 
active group
Setting Groups 5
All protection functions that could be available when setting group 5 the 
active group
Setting Groups 6
All protection functions that could be available when setting group 6 the 
active group