120-40 January, 2016
Model F120 UV/IR Flame Detector
MAINTENANCE
Factory Recommended Maintenance
The ame detector has been designed with very little to no required maintenance. Depending
on your application and safety guidelines in your facility, additional maintenance may be
necessary to ensure the installed equipment are functioning properly.
Periodic maintenance should be performed per the manufacturer’s recommendations and
instructions. Factory recommended regular maintenance schedule is as follows:
• Monthly Operation Test
• Quarterly Lens Cleaning
Annual Verication
Maintenance intervals should be independently established through a documented procedure
such as a maintenance log maintained by plant/safety personnel or third party testing services.
Monthly Operation Test
We recommend that a short performance test be performed at least every 30 days to verify
that your ame detector is operational. Even though the ame detector has a number of built-
in self checks, there can be cases where these checks cannot properly report a malfunction
in the detector.
Each ame detector should be tested with a source of UV and IR radiation on a periodic
basis to generate a test alarm.
Tools Required
Safety Systems Technology has specically designed a portable ame detector test lamp to
test its ame detectors.
SST Part # Description
194-1 Model FT194 Flame Detector Test Lamp with rechargeable batteries
and 120 volt battery charger, carrying case included
194-2 Model FT194 Flame Detector Test Lamp with standard “D” cell
batteries, carrying case included
194-3 Model FT194 Flame Detector Test Lamp with rechargeable
batteries and 240 volt battery charger, carrying case included
!
WARNING: The Model FT194 Flame Detector Test Lamp is not rated for use
in hazardous locations. De-classify the area to reduce the risk of ignition of
hazardous atmosphere. DO NOT use the test lamp where combustible and
ammable gases are present.