This parameter is not the efficiency of the motor but the ratio of the magnetizing current
to the total phase current of the motor. Lower power factor values will increase the
magnetizing current to the motor and thus increase the field strength resulting in tighter
control of the motor. Higher values decrease the magnetizing current and the field
strength.
If not known, a value of is recommended for high slip motors and a value of
is recommended for gearless induction motors.
This parameter is not applicable to PM synchronous motors and therefore will not appear.
LM07 Motor Torque
The rated motor torque in lb-ft or Nm, depending on selection of US02 System Units.
Motor Type
Range
Units
Default
Pass
Level
Ind.
PM
Min.
Max.
Imp.
Met.
RW
-
0
128000
-
Nm
5
Basic
-
RW
0
128000
-
Nm
5
RW
RW
0
94412.80015
lbft
-
3.699852507
LM07 is writable for both motor types: permanent magnet and induction.
For PM motors the torque value must be entered and is used to establish the torque
constant. Enter the rated name plate torque.
Since the desired unit for rated motor torque may not appear on the motor nameplate,
below are the appropriate conversions:
Unit
Conversion
lb-ft
HP x 5258 / Rated Speed (rpm)
lb-ft
kW x 7043 / Rated Speed (rpm)
lb-ft
Nm / 1.355
Nm
HP x 7125 / Rated Speed (rpm)
Nm
kW x 9543 / Rated Speed (rpm)
Nm
lb-ft x 1.355
LM08 Electric Motor Protection
This parameter is used to activate and select the type of motor overload function.
Depending on the setting of this parameter, the elevator drive 

Motor Type
Setting Options
NUM
Range
Units
Default
Pass
Level
Ind.
PM
Min.
Max.
Imp.
Met.
RW
RW
Electric Motor Protection
-
0
1
-
-
1
Basic
off
0
-
-
-
-
-
-
on
1
The trigger level is established in parameter LM09 Electric Motor Protection Current.

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the KEB F6 and is the answer not in the manual?

KEB F6 Specifications

General IconGeneral
CategoryInverter
Protection ClassIP20
Communication InterfacesPROFIBUS, CANopen, RS485
Operating Temperature-10°C to +50°C
SeriesF6
Output Frequency0 Hz to 600 Hz
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Short circuit
Humidity5% to 95% (non-condensing)
AltitudeUp to 1000 m above sea level
Control ModesSensorless vector control
Storage Temperature-25°C to +70°C

Related product manuals