EasyManuals Logo

KEB F6 User Manual

KEB F6
305 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Page #88 background imageLoading...
Page #88 background image
Parameter Descriptions
88
© 2024 KEB America, Inc.
Refer to US04 Control Type = Binary Speed Selection & Digital Speed
Selection for description of the basic operation.
The LI03 setting only changes the logic table according to the corresponding
US04 Control Type setting.
LI04 Input 1 Function
Used to limit the maximum speed of the lift in the event the emergency power generator
is not able to provide enough power to the elevator. Maximum speed is directly
proportional to maximum power draw on the AC line.
Input 1 corresponds to digital control terminal I1, X2A1.
Motor Type
Range
Units
Default
Pass
Level
Ind.
PM
Min.
Max.
Imp.
Met.
RW
RW
0
33
-
-
0
Basic
If this input is available, then it is free to be programmed with the one of the following
input functions:
Table 12. LI04 Input 1 function settings
Programmable Input
Functions for LI04 - LI11:
Description of Functionality:
NUM
No function
No function is assigned to input
0
UPS operation* **
The undervoltage limit is reduced and single phase
detection is turned off to allow for supply from 230V UPS
battery power source; the LS10 Battery Operation Speed
is selected. Additionally, carrier frequency is dropped to
2kHz to reduce switching losses at very low output
frequencies.
1
Reduced torque*
The torque limit is set according to the LC31 Reduced
Maximum Torque.
2
UPS + Reduced torque
Currently not implemented
3
Emergency profile*
Emergency Profile rate settings are loaded, according to
parameters LS40-45
4
UPS + Emergency profile
Currently not implemented
5
Reduced torque +
Emergency profile
Currently not implemented
6
UPS + Reduced torque +
Emergency profile
Currently not implemented
7
Emergency power speed*
LS09 Emergency Power Speed is selected and all speeds
are limited to this value
8
UPS + Emergency power
speed
Currently not implemented
9
Reduced Torque +
Emergency power speed
Currently not implemented
10

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the KEB F6 and is the answer not in the manual?

KEB F6 Specifications

General IconGeneral
CategoryInverter
Protection ClassIP20
Communication InterfacesPROFIBUS, CANopen, RS485
Operating Temperature-10°C to +50°C
SeriesF6
Output Frequency0 Hz to 600 Hz
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Short circuit
Humidity5% to 95% (non-condensing)
AltitudeUp to 1000 m above sea level
Control ModesSensorless vector control
Storage Temperature-25°C to +70°C