Speed for
Door Pre-
opening*
Output is set when the speed is below LX15 Speed for Pre-
Opening to allow pre-opening of the doors.
Output is set when less than 6 inches (15cm) from the floor.
Note: Floor position must be on.
Output is set when the speed and direction inputs are
signaled (direction only for analog and serial speed control
modes). Output turns off at end of run after the current has
ramped down and the drive enters Mode = No Direction (LS).
This output function cannot be used in combination with LI15
Direction Selection Inputs = Down (I6) Input Only.
Refer to LI04 Input 1 Function for further details on the
Main Contact Control.
Output is set when terminals T1 & T2 are open. Tells the
controller to stop at the next floor.
Output is set when the drive heatsink reaches 40 degrees
Celsius.
Output is linked to LO30-32.
Output activates when NTSD slowdown is triggered and
remains on until the direction is dropped or until the
command speed is below the TS02 NTSD Target Speed
(analog or serial speed control).
This output indicates there is a critical malfunction of the
Brake transistor. This output condition switches on when the
value of the drive parameter ru01 is 117: ERROR Brake
transistor failure.
Default (LO05) = At Speed (5)
Default (LO10) = Deceleration Active (7)
Default (LO15) = Off (0)
Default (LO20) = OFF (0)
* Only one of these four conditions can be selected at a time.
LO05 Output Function O1
This output is available to be programmed with one of the following output functions listed
in Table 28.