Parameter Reference
276
© 2024 KEB America, Inc.
Para.
Name
Adr
Motor Type
Setting Options
Num
Range
Units
Default
Pass
Level
Ind.
PM
Min
Max
Imp.
Met.
LL15
Overspeed Test
0x098F
RW
RW
Tune Activation
-
0
2
-
-
0
Basic
0
-
-
-
-
-
-
OFF
1
Start
2
Tune Active
3
Tune State
-
off
0
USER: Run elevator at High Speed or
Inspection Speed. The elevator will overspeed
16
STATUS: Running elevator at overspeed
32
SUCCESS: Overspeed test complete
160
Cannot start tune because another tune mode
is already active
176
LL16
Overspeed Test Speed
0x0990
RW
RW
-
-
0
12.2
-
m/s
0
Basic
0
2400
ft/min
-
0
LL17
Safety Release
0x0991
RW
RW
Tune Activation
-
0
2
-
-
0
Basic
0
-
-
-
-
-
-
OFF
1
Start
2
Tune Active
3
Tune State
-
off
0
USER: Acceleration and start jerk increased.
Run elevator at High Speed or Inspection
Speed.
16
STATUS: Running elevator
32
SUCCESS: Safety release complete
160
Cannot start tune because another tune mode
is already active
176
LL18
NTSD Tune Mode
0x0992
RW
RW
Tune Activation
-
0
255
-
-
0
Basic
0
-
-
-
-
-
-
OFF
1
Start
2
Tune Active
3
Tune State
-
off
0
USER: Run elevator at High Speed, from
terminal landing to terminal landing
16
STATUS: Running elevator
32
USER: Accept the learned thresholds?
48
FAILURE: No NTSD input was activated
64
SUCCESS: NTSD Tune complete
160
Cannot start tune because another tune mode
is already active
176
User Input
-
0
Yes
4
No
8
Waiting for input
12