SMOKE SENSOR SETUP
SMOKE SENSORS
Smartrise controllers include four inputs for connecting smoke sensors. In a 4-
Smoke setup activation of any smoke sensor will put the controller in Fire Recall
operation. In a 3-Smoke setup only Smokes 1 & 2 will put the controller in Fire
Recall operation.
The inputs are: Smoke 1, Smoke 2, Smoke 3, and Smoke 4. See Sheet 2 of the job
prints to determine which SRU board input is configured for each smoke
designation.
During installation, the smoke inputs should temporarily be jumped to M24 until
such time as the smoke sensors are installed. The jumper must be removed when
the smoke sensor is connected. Leave the jumper in place on any smoke input
which will not be used.
Smartrise recommends wiring and programming the smoke inputs in the following
manner for proper compliance with A17.1/B44 safety code. The following table
illustrates the sensor number, the location the sensor is installed and where the car
goes to during activation.