NORMAL/DIRECTIONAL LIMITS
These limits are physical switches electronically calculated by the Smartrise board
and activated at the outside edge of the terminal landing DZ magnets.
1. Run the car on inspection toward the last door zone in either direction
and verify that the car stops in the direction of travel when it reaches the
last edge of the last door zone magnet.
a. If the floor level is in the middle of the magnet then the limits are
3 inches below the magnet for the bottom terminal -- 3 inches
above for the top magnet. If 3 inches of over-travel is too much,
simply move the bottom magnet(s) up more and move the top
magnet(s) down more in order to achieve your desired result.
b. If magnets are moved in step 1.a then a “Learn” procedure will
have to be performed and floor height settings readjusted at these
locations.