LEVELING SPEED TEST (V2.35E OR NEWER ONLY)
1. Navigate to MAIN MENU | SETUP | SPEED AND SLOWDOWNS | LEVELING
SPEED and change the speed to a value greater than 150 FPM. Save this
value.
2. After saving the new value, you should get a ‘F161: Invalid Parameter’ fault
in Active Faults. This indicates that the leveling speed is outside its proper
operational range.
3. Change the leveling speed back to the original value and save. The fault will
automatically reset.
LEVELING ZONE TEST
1. Enter a car call to the bottom landing using MAIN MENU | DEBUG | ENTER
CAR CALLS and put car in Inspection (MR) Mode.
2. Move the car in Inspection Mode about a foot above the bottom landing.
3. Open the doors using MAIN MENU | SETUP | DOOR SETUP | MANUAL OPEN
& CLOSE.
a. Move asterisk under Open and press and hold the Enter button on
the SRU controller. The door icon “[ | ]” will change to “[ < | > ]”
while opening and then to “< >” when they’re fully open. Release the
Enter button at this time and the doors will remain open.
4. Move the Inspection switch back to Normal Mode.
5. Verify that the doors close prior to the car moving. After the doors close the
car will move back to the door zone (DZ) in leveling speed.