205
OTHER ADJUSTMENTS
ACCESS TOP/BOTTOM LIMITS:
1. To set the access distance, simply adjust the parameters ACCESS DIST TOP
and ACCESS DIST BOTTOM located under MAIN MENU | SETUP.
POSITION INDICATOR VIA CE:
1. Floor labels can be programmed at MAIN MENU | SETUP | PI LABELS if a CE
micro-com or Emotive fixture is installed.
RESYNCHING - HYDROS
1. Set real-time clock time/date at MAIN MENU | SETUP | REAL-TIME CLOCK
2. Set releveling to Yes in MAIN MENU | SETUP | FLOOR LEVELS | RELEVELING
3. Set resynch start time at MAIN MENU | SETUP | MISC | RESYNCH START
TIME
4. Set resynch duration at MAIN MENU | SETUP | MISC | RESYNCH DURATION
SIMPLEX PARKING SETUP
1. Go to MAIN MENU | SETUP | GROUP SETUP | PARK DELAY TIME to setup the
delay time until the car goes into park mode (000 secs)
2. Parameter 00-083 sets the park floor in MAIN MENU | DEBUG | ADJUST
PARAMETERS
a. (x00 = bottom floor, x02 = 2
nd
floor, etc.)
b. Example: PI for a 4 stop is labeled: G, L, 2, 3
i. 00-083 = x00 car will park at G,
ii. 00-083 = x01 will park car at L, etc.
HYDRO RUPTURE SETUP
2. If you need to setup and adjust the rupture valve you need to move the car
down in a multi-floor run at the highest speed possible.
a. If your Contract speed is < 150fpm then you can increase your inspection
speed to 150fpm and run it the car on Inspection.
b. If your Contract speed is > 150fpm then you have to run the car in
Normal mode. You can place car calls using MAIN MENU | DEBUG |
ENTER CAR CALLS