233
F80
DETS Overspeed
Overspeed of Car at DET switch.
Causes
Extra Bytes A or B : Commanded car speed was 95% of Contract Speed as car crossed an ETS
switch while approaching the terminal.
Extra Bytes C or D : Actual detected car speed was 95% of Contract Speed as car crossed an
ETS switch while approaching the terminal.
Remedies
Increase the slowdown distance parameters.
Move the ETS switch that caused the fault closer to the terminal.
Increase the slowdown distance parameters.
Move the ETS switch that caused the fault closer to the terminal.
F81
UETS Overspeed
Overspeed of Car at UET switch.
Causes
Extra Bytes A or B : Commanded car speed was 95% of Contract Speed as car crossed an ETS
switch while approaching the terminal.
Extra Bytes C or D : Actual detected car speed was 95% of Contract Speed as car crossed an
ETS switch while approaching the terminal.
Remedies
Increase the slowdown distance parameters.
Move the ETS switch that caused the fault closer to the terminal.
Increase the slowdown distance parameters.
Move the ETS switch that caused the fault closer to the terminal.
F91
Learn Error
Learn Error
Causes
The LEARN MAGNETS command was given when car was not in the bottom door zone.
Controller must see DZ on, DET off, and UET on to begin the learn process.
Remedies
Verify the LEARN MAGNETS command is given only when car is at bottom door zone.
Verify the door zone input is correctly wired and magnets are reading properly.
Verify DET and UET are installed correctly and do not overlap with any door zone magnets.