EasyManua.ls Logo

Smartrise F220

Default Icon
279 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Loading...
241
F151
Passcode
The passcode required for normal operation is not entered
Causes
The passcode required for normal operation is not entered.
Remedies
Contact Smartrise for access to the passcode.
F160
Critical Params
One or more of the “critical” parameters is not valid
Causes
One or more of the following parameters is not set to a valid value:
Number of floor
Controller type
Number of car doors
Number of controller boards
Remedies
After a power-on or board reset, this fault may come on briefly. If the fault clears right away
then no action is required.
If the fault persists, you may need to default the parameters by selecting MAIN MENU | SETUP
| DEFAULT ALL.
F161
Invalid Params
One or more of the “critical” parameters is not valid
Causes
Extra Bytes 1-0: No Run Speeds set.
Extra Bytes 2-0: Non-ascending Run Speeds.
Extra Bytes 3-0: One or more of the Run Speeds is set to a value greater than 900 fpm.
Extra Bytes 4-0: Inspection Speed set greater than 150 fpm. To comply with A17.1 code,
inspection speeds above 150 fpm are not allowed.
Extra Bytes 5-0: Unused Run Speeds not set to zero.
Remedies
Extra Bytes 1-0: There are eight available Run Speeds (S1-S8). You must set at least one with a
non-zero value.
Extra Bytes 2-0: The speed defined by S2 must be larger than S1. Likewise S3 must be larger
than S2. This applies to all non-zero Run Speeds. All unused Run Speeds must be set to zero.
Example:
S1 = 50 fpm
S2 = 175 fpm
S3 = 300 fpm
S4 ~ S8 = 0
Extra Bytes 3-0: Reduce the offending Run Speed to less than 900 fpm or contact Smartrise for
software to support higher speeds.
Extra Bytes 4-0: Reduce Inspection Speed to 150 fpm or less.
Extra Bytes 5-0: Set all Run Speeds above highest one used to zero.

Table of Contents

Related product manuals