245
F217
Rnd Governor
Causes
Obsolete. No longer logged.
Remedies
N/A
F218
Safety String
Safety String is open
Causes
Relay SS is de-energized because the safety string has lost power.
Remedies
Verify that all stop switches, final limits, and other contacts in the safety string (see job
specific drawings) are in the closed position.
F219
Flood Sensor
Causes
The elevator has been taken out of service at an upper floor due to flooding.
Remedies
Verify that flood sensor is operating and wired correctly.
If Flood Sensor is not required, place a permanent jumper from M24 to Flood Sensor input
terminal on Machine Room SRU.
F220
UET and DET
Both UET and DET are active
Causes
Both ETS switches are in the active state.
Remedies
Check the switches and controller input terminals. Check the CAT5 cable connections
between the IP8300 selector and the breakout board.
F221
Redundancy
Causes
This error is normally caused by the jumpers (J24) or Dip Switch settings being set wrong.
Remedies
Check the Jumpers and Switches on each board and verify correct settings with the
drawings specific to that board.
F222
Relay Feedback
Causes
The software and the safety hardware circuit are not seeing the same feedback from one of
the safety
Remedies
The first of the two extra bytes shows the SRU input terminal (1=501, 2=502, etc.)
monitoring.