CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES 4.1 ENERVISTA 650 SETUP SOFTWARE
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 4-23
Table 4-8: Control elements menu, firmware version 7.50 and above
4.1.7.7 Inputs/Outputs menu
Section that contains the settings for all input and output boards and the Force Outputs and Virtual inputs activation tools.
(*) indicates online only, (**) indicates offline only
This section shows the settings related to inputs and outputs for the different boards available in F650 (F, G, H, J)
Control Elements
Setting Group F650 incorporate a flexible grouping capability for protection units can be used in either
single setting group (default mode- All units that belong to Active group, configured in
Setpoint > Control > Setting Group, can operate simultaneously ) or up to six setting groups
(in this mode, all protection elements, that are available when setting group function is
disabled, will be available in each individual setting group (Up to maximum of 6). Only one
of setting group will be active at a given time). Units grouped under Protection elements
section will be the units affected by changing of setting group.
Synchrocheck Synchronism check unit (25). Single element.
Autoreclose Recloser (79). Single element.
Breaker Failure Breaker failure (50BF). Single element.
VT Fuse Failure Fuse Failure (VTFF). Single element.
Pulse Counters Pulse counters function. 8 counters provided.
Analog Comparators Analog comparator function. 20 analog comparators provided.
Max. Number of Starts Maximum Number of Starts (66). Single element.
Digital Counters Up to 8 Digital Counters
Cold Load Pickup Cold Load Pickup Function. Single element. Available for firmware version 7.00 and above.
PLC Timer Masks Configuration of masks that can be assigned to PLC timers
60 CTS Failure Current transformer failure function
2nd HRMC Inhibit Second harmonic inhibit
Inputs/Outputs
Contact I/O Inputs and outputs settings for all boards in F650. The I/O settings configuration can only
be performed through EnerVista 650 Setup, not available through the HMI.
Force Outputs (*) This menu allows activating each contact output in the relay, to facilitate maintenance
testing. Online mode only.
Virtual Inputs (*) This menu allows operating virtual inputs. These variables are used as inputs to logic
schemes configured in the relay. Virtual inputs can be operated in a latched mode (32
latched virtual inputs) or in Self-reset mode (32 self reset virtual inputs).
Remote Comms. This menu allows configuring remote inputs coming from other devices and allow
enabling None, GSSE or GOOSE messages. Available for IEC61850 (6) models only.
Contact I/O
Board F Board located in first slot, always connected.
Board G Board located in second slot, depending on model definition. If model is type G0 there is no
board in second slot.
Board H Board located in first slot of CIO Module (external inputs/outputs module)
Board J Board located in second slot of CIO Module (external inputs/outputs module)