CHAPTER 5: SETPOINTS 5.2 PRODUCT SETUP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-11
"SNTP1 tab shall contain settings of main SNTP server.
"SNTP2 tab shall contain settings of back-up SNTP server.
If two SNTP servers are configured, F650 operation mode is described as follow:
NOTE: SNTP settings take effect after rebooting the device.
5.2.1.7 Procome protocol settings
Communication settings for Procome protocol. For more detail information go to APPENDIX E in this manual.
When NONE is selected in the comm port setting the protocol is not enabled. The com1 selection enables Procome for the
com1 (remote) serial port.
Slave Number:is the Procome slave number.
Baud rate and parity for COM1 must be set in the Setpoint>Communications>Serial Ports menu.
5.2.1.8 IEC 870-5-103 protocol settings
Communication settings for IEC 60870-5-103 protocol. For more detailed information go to 5.13 Section in this manual.
DNP protocol is available for standard and IEC61850 models but it is not available IEC 60870-5-103 models.
If COMM Port is set to NONE, IEC 870-5-103 communication protocol is not available.
If the user sets a value different from 0 in the Synchronization Timeout setting, when this timer expires without receiving a
synchronization message, the Invalid bit is set in the time stamp of a time-tagged message.
Scenario Expected behaviour
SNTP1 server= Available
SNTP2 server= Available
F650 shall be synchronized by SNTP1 server.
No alarm
SNTP1 server= Available
SNTP2 server= Not Available
F650 shall continue to be synchronized by SNTP1 server
No alarm
SNTP1 server= Not Available
SNTP2 server= Available
If SNTP1 server fails, F650 shall get synchronization from SNTP2
ser
ver. When SNTP1 server recovers, F650 shall switch to be
synchronized by SNTP1 server.
No alarm
SNTP1 server= Not Available
SNTP2 server= Not Available
"Not Syncronized" Alarm shall appear in local mimic
Product Setup > Communication settings >PROCOME
Name Default Value Step Range
COMM Port NONE N/A [NONE - COM1]
Slave Number 0 1 [0 : 254]
Product Setup > Communication settings >IEC 870-5-103
Name Default Value Step Range
COMM Port NONE N/A [NONE - COM1]
Slave Number 1 1 [0 : 254]
Synchronization Timeout 30 min 1 [0 : 1440]