D-10 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
D.5 IEC 60870-5-104 POINT LIST APPENDIX D: IEC 60870-5-104 PROTOCOL
D.5 IEC 60870-5-104 point list
OPERATIONS IN IEC 60870-5-104 FOR F650
The two standard procedures for command transmission are accepted, Direct command or Select and Execute command.
The following table determines how a command can be executed in F650
There are 24 available operation in F650 device; they must be configured using EnerVista 650 Setup in Setting
> Relay Configuration > Operations.
ASDU address must start with 3000; the addresses for operation are from 3000 to 3011. The operations go from 0 to 23.
Commands
POINT DESCRIPTION COMMAND MODE
3000 Operation 1 (ON) + Operation 2(OFF) Select and Execute Double Command
--- --- ---
3005 Operation 11 (ON) + Operation 12(OFF) Select and Execute Double Command
3006 Operation 13 (ON) + Operation 14(OFF) Direct Double Command
--- --- ---
3011 Operation 23 (ON) + Operation 24(OFF) Direct Double Command
3012 Virtual Self Reset 1 (ON) + Virtual Self Reset 2(OFF) Direct Double Command
--- --- ---
3027 Virtual Self Reset 31 (ON) + Virtual Self Reset 32(OFF) Direct Double Command
3028-3059 Virtual Latched 1-32 Direct Single Command