10-14 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
10.13 DIRECTIONAL ELEMENTS (67P, 67N, 67G, 67SG) CHAPTER 10: COMMISSIONING
10.13 Directional elements (67P, 67N, 67G, 67SG)
In order to test directional units in the relay, instantaneous trips are commanded.
Two points are tested, per phase, test element.
In order to test the directional units, configure (in the Setpoint > Relay Configuration > Protection Elements screen of the
EnerVista 650 Setup program), some overcurrent element to be supervised by a directional unit. This way, if the directional
element is enabled and detects the fault in the block direction, then the overcurrent unit does not operate. If the directional
element is not enabled or if it is enabled and it detects a fault in a trip direction, then the overcurrent unit operates if the set
current level is exceeded.
10.13.1 67P element
Activate only protection elements 50PH and 67P and set the relay as follows:
Configure one of the outputs to be activated only by unit 50PH.
Apply the following tests:
10.13.2 67N element
Activate only protection elements 50N and 67N and set the relay as follows:
Configure one of the outputs to be activated only by unit 50G.
67P Settings 50PH Settings
Function ENABLED Function ENABLED
MTA 45 Deg Input PHASOR (DFT)
Direction FORWARD Pickup Level 0.50 A
Block Logic PERMISSION Trip Delay 0.30
Pol V Threshold 30 V Reset Delay 0.00
Elements Phase under test Polarization Phase Element trip
Channel Magnitude Channel Magnitude
Mod Arg Mod Arg
50PH/67P IA 2 A 0º VIII
60 V
0º NO
60 V
180º YES
IB 2 A 0º VI
60 V
0º NO
60 V
180º YES
IC 2 A 0º VII
60 V
0º NO
60 V
180º YES
67N Settings 50N Settings
Function ENABLED Function ENABLED
MTA -45 Deg Input PHASOR (DFT)
Direction FORWARD Pickup Level 0.50 A
Polarization VO Trip Delay 0.30
Block Logic PERMISSION Reset Delay 0.00
Pol V Threshold 10 V