5-144 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
5.6 INPUTS/OUTPUTS CHAPTER 5: SETPOINTS
5.6.5.3 Without supervision
This is a very frequent common case, and we must only wire the tripping circuit to terminals F35 and F36, leaving unused
terminals F34, F15, F16, F17, F18.
Figure 5-38: Circuit without tripping circuit supervision (A6631F1)
5.6.5.4 With current supervision (with SEAL-IN)
In this case, as shown in Figure 5-39: Current supervision of the tripping contact (A6631F2), the current supervision circuit
consists of a circuit connected in series with the output contact, so that the external circuit is wired to terminals F34 and
F36. This supervision circuit includes a low impedance reed relay that is activated when the current value exceeds 200 mA,
and sends a signal to the main microprocessor. This latches the output relay in such a way that this indication can be used