6-2 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
6.2 STATUS CHAPTER 6: ACTUAL VALUES
6.2 Status
6.2.1 Operation bits status
(Actual > Status > Operation bits)
OPERATION BIT 1...24 These 24 bits are the outputs of each possible Operation modules, programmed in menu
Setpoint > Relay Configuration > Operations. The light up LED indicates their status 1
(activation)
6.2.2 Breaker status
The signals associated with the opened or closed status of the breaker can be monitored at Actual > Status > Breaker
BREAKER OPEN: Open breaker status. In the switchgear selected as breaker, besides providing the usual
switchgear contact status, the system provides also the open breaker, closed breaker, and
undefined breaker states.
BREAKER CLOSED: Breaker closed.
BREAKER UNDEFINED: If there are two digital inputs configured for breaker contacts 52/a and 52/b, this status is present
when both inputs are at 0 or at 1. This status can be caused by a wiring failure, failure of auxiliary
elements, etc.
LED 14
LED 15
LOCAL OPERATION MODE
OPERATIONS BLOCKED
ST HMI BACKLIGHT
OPERATION BITS
OPERATION BIT 1
OPERATION BIT 2
OPERATION BIT 24
BREAKER STATUS
BREAKER OPEN
BREAKER CLOSED
BREAKER UNDEFINED