GEK-106310-AF F650 DIGITAL BAY CONTROLLER 11-1
F650 Digital Bay Controller
Chapter 11: Application examples
GE
Grid Solutions
APPLICATION EXAMPLES
11.1 Example 1: Communication & protection settings
11.1.1 Description
The requirements for this setting exercise are:
Communicate the relay via serial cable or Ethernet 10/100 Base T cable using EnerVista 650 Setup program.
Set some Phase Time Overcurrent protection function to operate at 5A, Inverse curve IEC, Dial 0.1
Set some Output contact on board F to be operated and sealed by the operation of the phase TOC.
Set some LED to show the operation of the phase TOC
Set some Operation to reset the output contact after dropout of the phase TOC since the front F1 pushbutton.
Set some Oscillography channel to record the pickup of phase TOC and output contact closing action.
To test the operation of this Phase Time Overcurrent protection
11.1.2 Communicate with the relay
This procedure describes the connection between any Laptop and some F650 relay using the EnerVista 650 SETUP
program
For any one of these connections check first the communication parameters as follows:
Serial Communication (RS232 or USB front port of the relay)
With the ESC key check on the main front screen the serial communication parameters (Baud rate, parity, data bits, stop
bit and ID number).
Connect the serial cable PC-F650
Open the EnerVista 650 SETUP program in the PC and under Communication Computer menu check that the serial
communication parameters displayed are the same read in the front of the relay. Check also that:
Control Type is set to No Control Type
Startup Mode is set to Communicate with relay