CHAPTER 6: ACTUAL VALUES 6.2 STATUS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 6-17
For each of the 8 digital counters, there exist independent and identical groups of actual values:
• DIGCNT # HI [OFF: ON]: If this bit is activated, the counte
r value DIGCNT # VALUE is greater than the setting DigCNt
#Compare value.
• DIGCNT # EQ [OFF: ON]: If this bit is activated, the counter value DIGCNT # VALUE is equal than the setting DigCNt
#Compare value.
• DIGCNT # LO [OFF: ON]: If this bit is activated, the counter value DIGCNT # VALUE is lower than the setting DigCNt
#Compare value.
(These 3 previous states are mutually exclusive: only one can be ON at the same time. If the counter is Disabled, the 3 of
them are OFF.)
• DIGCNT # VALUE [-2,147,483,648 : 2,147,483,647]: The specified counter current value.
• DIGCNT # FROZENVALUE [-2,147,483,648 : 2,147,483,647]: The specified counter last captured (frozen) value.
• DIGCNT # FROZENDATE [Valid date]: The specified counter last captured (frozen) date.
6.2.4.14 Cold load pickup
This screen can be accessed at Actual> Status > Control Elements >Cold Load Pickup, and it includes two LEDs for the
Cold Load Pickup function, indicating two magnitudes; pickup and trip (operation).
Table 6-23: Cold load pickup actual values
DIGCNT 8 VALUE
DIGCNT 1 FROZENVALUE
DIGCNT 2 FROZENVALUE
DIGCNT 3 FROZENVALUE
DIGCNT 4 FROZENVALUE
DIGCNT 5 FROZENVALUE
DIGCNT 6 FROZENVALUE
DIGCNT 7 FROZENVALUE
DIGCNT 8 FROZENVALUE
DIGCNT 1 FROZENDATE
DIGCNT 2 FROZENDATE
DIGCNT 3 FROZENDATE
DIGCNT 4 FROZENDATE
DIGCNT 5 FROZENDATE
DIGCNT 6 FROZENDATE
DIGCNT 7 FROZENDATE
DIGCNT 8 FROZENDATE
COLD LOAD
PICKUP
Cold Load PKP
Cold Load OP