5-158 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
5.9 RELAY CONFIGURATION CHAPTER 5: SETPOINTS
5.9.3 Operations
This menu option shows the settings for the 24 control operations that can be programmed, as follows:
Select checkbox enables the desired operation.
Command T
ext setting defines the command name.
Int
erlocks Type setting defines the desired interlock type (An interlock is a condition that must be fulfilled for an
operation to be performed). The possible options are Logic or None. If the LOGIC option is selected, the program
enables a new window for creating the logic. If the NONE option is selected, then the following setting (Interlocks) is
irrelevant.
Int
erlocks setting define the desired interlocks. This setting is enabled selecting the “logic” option in “Interlock type”.
In the “Interlock logic” screen we can set the interlock logic, as shown on Figure 5-48: Operations and interlocks
The settings on this screen allow creating a logic configuration with up to 3 AND gates and 1 OR gate for each of the
24 operations available in the relay. These settings are:
Select Enables/disables the selection for the interlock input
Source Selects a function, digital input, logic, etc. for defining each input of each AND gate.
NOT Logic inverter
Figure 5-48: Operations and interlocks
Final S
tate Type setting: defines whether the operation requires (in addition to the interlock logic) any other conditions
to determine a “success condition”. If so, we must select LOGIC. Otherwise, we must select NONE.
Final S
tate setting: defines the success condition of a programmed operation, if the previous setting (Final State type)
was set as LOGIC.
Fr
ont Key setting: defines the front pushbutton from which the operation can be executed.
Conta
ct Input setting: defines whether the operation can be executed by digital input. It defines the digital input to be
used for this purpose.
Vi
rtual Output setting: defines whether the operation can be executed from a virtual output previously defined at the
logic configuration tool (PLC logic).
Ti
me Out setting: defines the period during which the operation command remains activated waiting for a success
condition. If the success signal is received before this period expires, the command signal is removed and the timer
reset. If the success condition is not received within this period of time, the operation is considered to be finished.
H
MI setting: defines whether the operation can be executed by HMI