CHAPTER 5: SETPOINTS 5.13 IEC 60870-5-103 CONFIGURATION
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-193
5.13 IEC 60870-5-103 configuration
The IEC103 Configuration option is only be available if the F650 that supports this protocol (3 in the order code for protocol
selection). The IEC103 protocol for the F650 can be configured using the EnerVista 650 Setup program in the menu
Setpoint > IEC103 Configuration.
When opening the IEC103 configuration tool, either open a "f650iec103.cfg" configuration file or continue to the IEC103
configuration tool with no file selected. The IEC103 configuration can be retrieved from the relay by clicking Retrieve
Configuration. Changes can be saved to the configuration file, and then sent to the relay by clicking Send Configuration.
In order to start working with the new IEC103 configuration, the relay must be switched off and on.
The IEC103 slave can be identified (besides the slave number) with a long name (8 characters identifier) and with a short
name (4 characters identifier for the manufacturer's internal software release) that can be set in the IEC103 configuration
file.
Control data that can be configured includes: digital states, measurands and commands. Some IEC103 parameters can be
set in the configuration file and then sent to the relay
Digital states:
All the digital states that F650 supports are available in order to be mapped using the EnerVista 650 Setup program. All the
mapped information is sent as a response to a general interrogation.
In the interoperability table, the states that the standard propose have been selected with the suitable information
number. Some of them must be generated in the firmware code as an OR operation. This information is mapped by
default, but the user can delete them if desired. For the other states, you can assign the Information Number <1..255> and
the Function Type <0..255>, but the Identification Type 1 (Time-tagged message) is fixed.
To configure a new mapping of a digital state, set the Function Type and the Information number. Then select Digital
Status from the first combo box in the Status frame for mapping a single digital state, and the digital state to be sent
to the IEC103 master from the second combo box. You can configure a logic OR operation of digital states selecting
Logic in the first combo box and clicking Press for Logic. In the next screen, choose the digital status combination to
be sent to the IEC103 master and click Save.
Finally click Add and the configured data is added to the Status List.
To remove an existing signal from the status list, select the signal then click Remove. The signal is removed from the
status list.
In the same way, to change a configured signal from the status list, select the signal, make the changes, and then
cl
ick Update. The signal is updated in the status list
To save the data in the configuration file, click Save and
all the data is stored in the corresponding "*.cfg" file.