4-18 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
4.1 ENERVISTA 650 SETUP SOFTWARE CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES
4.1.7.1 Product setup menu
(*) indicates online only, (**) indicates offline only
4.1.7.2 Communication settings menu
This section details the settings related to communication parameters for the different protocols available in the F650.
(*) indicates online only, (**) indicates offline only
Product Setup
Communication
Settings
Serial Ports, Network (Ethernet), ModBus Protocol, DNP Slave, IEC 870-5-104, SNTP settings
and procome (if available on model selection), PTP1588 and Routing (for firmware version
7.00 and higher)
ModBus User Map ModBus user map definition. The ModBus user map is formed by 256 records, selectable
from the complete relay ModBus map.
Fault Report Fault report settings. Possibility to show fault reports on HMI screen.
Oscillography Oscillography settings (trigger position, samples per cycle, etc.). The trigger and digital
channels (up to 16) must be configured in Setpoint > Relay configuration.
Data Logger Data logger configuration
Demand Demand settings. The demand trigger and demand reset signals must be configured in
Setpoint > Relay configuration
Time Settings Time settings.
COMMUNICATIoN
SETTINGS
Serial Ports Baud rate and parity for COM1 and COM2 serial communication ports.
Network (Ethernet) Ethernet communication parameters for ETH_1/ETH2 or ETH_E/ETH_A/ETH_B
(Depending on model) (IP Address, Netmask, Gateway IP)
NOTE: The ModBus Slave address used by Ethernet ports is the one set for
C
OM2.EnerVista 650 Setup software allows programming two different Ethernet
addresses, but the first IP has always to be set as the second IP Address is an Alias.
ModBus Protocol ModBus Slave Addresses for serial and Ethernet communication and the ModBus port
number used for ModBus TCP/IP
DNP3 Slave Physical port, Slave Address for DNP, IP Addresses for Masters, TCP/UDP Port,
Unsolicited Response parameters, Analog scale factors and deadbands, message
fragment size, Binary input block.Available for standard and IEC61850 models.
IEC 870-5-104 TCP Port, Common Addr of ASDU, Cyclic Meter Period and, Synchronization Event
settings.Available for standard and IEC61850 models.
SNTP (*) Synchronization over Ethernet settings
PROCOME
Comm port and slave number for procome protocol. Only available for
procome models (5).
PTP 1588 Precission Time Protocol 1588 settings. (Available on fw version 7.00 or higher)
Routing A default route and a maximum number of 6 static routes may be configured. The
default route is used as the last choice, if no other route towards a given destination is
found.This option is only available for version 7.00 and higher.