5-140 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
5.6 INPUTS/OUTPUTS CHAPTER 5: SETPOINTS
5.6.4 Outputs
Output settings description
Output Logic_0X _0Z: Type of logic applied to outputs. Possible values are positive and negative. The default value is
positive. Depending on the type of setting selected, the physical output is in the same direction (positive) or opposite
(negative) the output activation command.
Output Type_0X _0Z: Type of output adjusted. Possible values are normal, pulse or latched, the default value is Normal.
Normal: The contact output follows the activation command. Remains active while the operation signal is active.
Pulse: The contact output is active the pulse output time, according to the Pulse Output Time setting.
Latched: The output remains active after the operation signal has been cleared. The reset signal for the latched
outputs is configured at Setpoint > Relay Configuration > Outputs > Contact Output Reset”.
Pulse Output Time_0X _0Z: This is the length of the output pulse in case the output type is selected as pulse; the default
value is 10000 ms.
Figure 5-36: Output logic typesshows the types of signals associated with the different output configuration types.
Figure 5-36: Output logic types
5.6.4.1 Output status signals
Boards types 1 and 2 have both 8 outputs, so the representation is the same for both types as shown in Table 5-86:
Contact output signals
Actual > Inputs/Outputs >Contact Output Status
Real status of the contact output, which corresponds to the transformation of the output activation signal (Contact output
operate), by the logic applied to this output in Setpoint > Inputs/Outputs >Contact I/O > Board X
Actual > Inputs/Outputs > Contact Output Operates
Activated or deactivated status of those variables used internally to operate a contact output.
Actual > Inputs/Outputs > Contact Output Resets