CHAPTER 5: SETPOINTS 5.3 SYSTEM SETUP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-31
5.3 System setup
This section shows the settings related to the system setup definition.
5.3.1 General settings
This section determines the settings of the element configuration regarding its connection to the power system.
The system rated voltage is used as reference by the voltage restraint in the phase timed overcurrent element.
The Frequency reference marks the voltage channel to which the system Frequency is measured.
The auxiliary voltage setting can be selected between VN and VX.
VN means that all elements using neutral voltage take the value directly from the fourth voltage input.
VX means that all elements using neutral voltage take the value calculated from phase voltages.
5.3.2 Miscellaneous settings
This section determines the relays status configuration regarding the service and local or remote modes.
5.3.2.1 Out of service setting
The unit Relay Out of Service setting is configured in Setpoint > System Setup > Miscellaneous. The unit also has an Out
of Service status that is configured in Relay configuration > Protection elements. When active, these states stop all
changes to PLC equations and functions, including changes in the input/output boards, so if there is a change in any input
Setpoint > System Setup > General settings
setting Description Name Default Value Step Range
Phase CT ratio Phase CT Ratio 1.0 0.1 [1.0 : 6000.0]
Ground CT ratio Ground CT Ratio 1.0 0.1 [1.0 : 6000.0]
Sensitive ground CT ratio Stv Ground CT Ratio 1.0 0.1 [1.0 : 6000.0]
Phase VT ratio Phase VT Ratio 1.0 0.1 [1.0 : 6000.0]
Phase VT connection Phase VT Connection WYE N/A [WYE – DELTA]
Rated voltage Nominal Voltage 100.0 0.1 [1.0 : 250.0]
Rated Frequency Nominal Frequency 50 Hz N/A [50-60]
Phase rotation Phase Rotation ABC N/A [ABC – ACB]
Frequency reference Frequency Reference VI N/A [VI-VII-VIII]
Auxiliary Voltage Auxiliary Voltage VX N/A [VX – VN]
Snapshot Event generation Snapshot Events DISABLED N/A [DISABLED – ENABLED]
Primary Meter Units Primary Meter Units KA_KV N/A [KA_KV; A_V]
Device Name Device Name N/A
Setpoint > System Setup > MISCELLANEOUS settings
setting Description Name Default Value Step Range
Relay Out of Service Relay Out of Service ENABLED N/A [DISABLED – ENABLED]
Local/Remote Blocked Local/Remote Blocked OFF N/A [ON -OFF]
Active Language Active Language 0 N/A [0;1]