4-44 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
4.2 HUMAN-MACHINE INTERFACE (HMI) CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES
To enter this menu press the shuttle key or enter key when the option Actual Values is selected in main menu. A secondary
level is displayed with different sublevels as shown on . Pressing Up/down keys or rotating the shuttle key, (left for moving
up and right for moving down) select the next level to be displayed, press the enter/shuttle key again to enter in next level
and press ESC key to return to previous level if desired. This navigation is performed the same for all the menus in Actual
Values. Once the last sublevel is reached, move up and down to visualize the actual values selected.
One example of data screen for actual values is shown in Figure 4-23: Actual values screen data.
First Line: Header of last level in actual values (Phase Current in the example)
Second Line: Data identifier (in the example PH IOC1 HIGH A, is the pickup signal for the first instantaneous overcurrent
function level high for phase A).
Third line: Status of the displayed actual value.
Fourth Line:Relative position in the menu (it is the first value of 114)
Figure 4-23: Actual values screen data
In the Actual Values menus are different types of data; each type of data displays its particular status type (on and off, 0 or
1, OK or fail, analog values, etc.)
4.2.6.4 Snapshot events
To enter this menu press the enter/shuttle key when the option Snapshot events is selected in main menu (). In this menu
all the snapshot events stored can be displayed.
Snapshot events are changes in the relay internal status.
One snapshot event is displayed in two text screens:
The first screen display the status, date and time of the snapshot event: the snapshot event identifier, its status, event
number and the date and time of the occurrence. If the snapshot event identifier does not fit the first line, the whole text is
shown using as well the second line alternating with the status and event number.
The second screen displays currents and voltages in primary values for that particular snapshot event. Ia, Ib, Ic and Ig for
currents and Vab, Vbc, Vca and V0 for voltages. To access the metering screen in snapshot events menu, press shuttle key
from the snapshot event first screen. To exit from the metering screen press ESC.
To select different snapshot events to be displayed, press the up-down keys or rotate the shuttle key to select the
snapshot event and then press the enter/shuttle key to enter the metering screen. Press esc to exit the metering screen
and return to snapshot events menu.
IO Board Status
Virtual Inputs > Virtual Inp.Latched
Virtual Inp.SR
Virtual Outputs
Remote Outputs (for
IEC61850 models only
) >
DNA
User St
GOOSE Dig Outputs
Remote Inputs for IEC61850
models only
)>
Remote Input
Remote Devices
GOOSE Dig Inputs
GOOSE Analog Inputs
Analog Inputs > Board F/ Board G/ Board H/ Board J
Virtual out. Latched
Virtual out. Analogue
Phase Current
PH IOC1 HIGH A PKP
OFF
(1/114)