CHAPTER 2: PRODUCT DESCRIPTION 2.5 TECHNICAL SPECIFICATIONS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 2-19
Number of Starts:..................................................................... 0 to 10 in steps of 1
Time to Restart: ........................................................................ 0 to 100 minutes in steps of 1 minute
Reset Counter:........................................................................... selectable by setting
Snapshot Events: ..................................................................... selectable by setting
Operate Time:............................................................................ < 45 ms at 50 Hz, typically
DIGITAL COUNTERS
Function: ...................................................................................... Disabled, Enabled
Name:............................................................................................ any 12 alphanumeric characters
Preset: ........................................................................................... -2147483648, 0, +2147483647
Compare:..................................................................................... -2147483648, 0, +2147483647
COLD LOAD PICKUP
Cold Outage Time:................................................................... 1 to 1000 minutes in steps of 1 minute
Cold Blocking Time: ................................................................ 1 to 1000 s in steps of 1 s
2.5.3 Monitoring
OSCILLOGRAPHY
Maximum Records:................................................................. up to 20 oscillography records
Sampling Rate:.......................................................................... programmable to 4, 8, 16, 32, or 64 samples per power cycle
Capacity per record:...............................................................
(27592 samples)/(number of oscillos x number of samples/cycle)
Maximum Records:................................................................. up to 20 oscillography records
Trigger Position:........................................................................ 5% to 95% of total length
Trigger:.......................................................................................... programmable via PLC
Data:............................................................................................... 5 current channels and 4 voltage channels up to 16 digital channels programmable
thr
ough PLC
Data Storage:............................................................................. non-volatile (flash) memory without battery
Format: ......................................................................................... International Standard COMTRADE ASCII - IEEE C37.111-1999
Automatic Overwrite:............................................................. selectable by setting (oscillography records can be concatenated)
Snapshot Events: ..................................................................... selectable by setting
FAULT LOCATOR
Method: ........................................................................................ single-ended
Positive Sequence Module: ................................................. 0.01 to 250.00 Ohm in steps of 0.01 Ohms
Positive Sequence Angle: ..................................................... 25 to 90º in steps of 1º
Zero Sequence Module:........................................................ 0.01 to 750.00 Ω in st
eps of 0.01 Ω
Zero Sequence Angle:............................................................ 25 to 90º in steps of 1º
Line Length:................................................................................ 0.0 to 2000.0 in steps of 0.1 miles or km (as per line length setting)
Accuracy:..................................................................................... 5% (typically)
Show Fault on HMI:................................................................. selectable by setting
Snapshot Events: ..................................................................... selectable by setting
Maximum Records:................................................................. up to 10 fault report records
Data:............................................................................................... Fault date and time, pre-fault currents and voltages, fault currents and voltages, fault
type, d
istance to the fault (fault location), line parameters, recloser and breaker status
information.
Data Storage:............................................................................. In non-volatile (flash) memory without battery available through communications In
v
olatile (RAM) memory available through HMI (if selectable by setting)
Format: ......................................................................................... text in ASCII format