CHAPTER 5: SETPOINTS 5.2 PRODUCT SETUP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-27
5.2.6.3 Demand function measurements and states
Demand values are available at Actual > Metering > Primary Values > Demand.
Table 5-11: Demand measurements
*Note: The step depends on the selected “Primary Meter Units” in System Setup > General Settings (A_V; KA_KV)
Demand measurements for current values are as follows:
DEMAND IX This is the demanded value every minute or every integration period, depending on the
selected settings.
DEMAND IX MAX Demanded maximeter; it stores the Maximum demand value until a demand reset is
issued.
DEMAND IX DATE Date of the Maximum demand value
Being X the phase considered in each case.
Demand measurements for power values are as follows:
DEMAND Y This is the demanded value every minute or every integration period, depending on the
selected settings
DEMAND Y MAX Demanded maximeter; it stores the Maximum demand value until a demand reset is
issued.
DEMAND Y DATE Date of the Maximum demand value.
Name Default Value Step
DEMAND IA 0.000 KA
DEMAND IA MAX 0.000 KA
DEMAND IA DATE 01-Jan-2000 00:00:00.000
DEMAND IB 0.000 KA
DEMAND IB MAX 0.000 KA
DEMAND IB DATE 01-Jan-2000 00:00:00.000
DEMAND IC 0.000 KA
DEMAND IC MAX 0.000 KA
DEMAND IC DATE 01-Jan-2000 00:00:00.000
DEMAND IG 0.000 KA
DEMAND IG MAX 0.000 KA
DEMAND IG DATE 01-Jan-2000 00:00:00.000
DEMAND ISG 0.000 KA
DEMAND ISG MAX 0.000 KA
DEMAND ISG DATE 01-Jan-2000 00:00:00.000
DEMAND I2 0.000 KA
DEMAND I2 MAX 0.000 KA
DEMAND I2 DATE 01-Jan-2000 00:00:00.000
DEMAND W 0.000 MW
DEMAND W MAX 0.000 MW
DEMAND W DATE 01-Jan-2000 00:00:00.000
DEMAND VAR PWR 0.000 MVAr
DEMAND VAR MAX 0.000 MVAr
DEMAND VAR DATE 01-Jan-2000 00:00:00.000
DEMAND VA PWR 0.000 MVA
DEMAND VA MAX 0.000 MVA
DEMAND VA DATE 01-Jan-2000 00:00:00.000