4-30 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
4.1 ENERVISTA 650 SETUP SOFTWARE CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES
Table 4-11: Control elements, actual values menu, firmware version 7.50 and above
Table 4-12: Records status, actual values menu
4.1.8.3 Metering
The Metering menu includes all the measurements available in the device. Primary and secondary values, and also the
data related to the recording functions in the relay
Control Elements
Frequency Status signals (pickups and operations) for under, overfrequency and frequency rate of
change units.
Synchrocheck Status signals for synchrocheck function (25).
Autoreclose Status signals for autoreclose function (79). Close signal, recloser status (ready, lockout, etc.),
block signals after each shot.
Breaker Failure Status signals for breaker failure function (50BF).
VT Fuse Failure Fuse failure detection signal.
Broken Conductor Status signals (pickups and operations) for broken conductor (I2/I1).
Setting Groups Status signals (activations and blocks) for the relay setting group change. By default the
Setting Groups setting is disabled and all the grouped elements can be enabled at the same
time.
Locked Rotor Status signals (pickups and operations) for locked rotor units.
Pulse Counters Status signals for pulse counters units.
Analog Comparator Status signals for analog comparator units.
Load Encroachment Status signals (pickups and operations) for load encroachment units.
Max. Number of Starts Status signal for number of starts operations
Digital Counters Status signals for the Digital Counter units.
Cold Load Pickup Status signals for the Cold Load Pickup Function.
60CTS Failure Status signals of Current transformer failure Function
2nd HRMC Inhibit Status signals of Second Harmonic Inhibit Function
Record Status
Fault Reports This menu shows the fault report status signals, as fault report trigger, fault date, fault type
and location, besides the fault report number.
Control Events Status of the control events (if the signal configured to launch the control event is active or
not).
Oscillography Status of signals related to oscillography recording, such as status or digital channels,
oscillography trigger, number of records available, etc.
Data Logger Data logger information about oldest and newest sample time stamp, and number of
channels and days configured in data logger settings.
Demand Demand trigger and reset inputs status.
Energy Freeze, unfreeze and reset input signals for energy counters.
Breaker Maintenance
All signals related to breaker maintenance, such as number of openings, closings, (KI)
2
t
counters, alarm signal for (KI)
2
t, etc.
metering
Primary Values Primary values measurements for currents, voltages, power, energy and demand
Secondary Values Secondary values measurements for currents, voltages and power.
Phasor Diagram Current, voltage and sequence components.
Frequency Line and Bus frequencies.