CHAPTER 10: COMMISSIONING 10.17 RECLOSER (79)
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 10-23
10.17.2 Recloser status
BLOCK
Activate the block input and verify that the recloser is in BLOCK status.
Close the breaker and wait for 5 seconds.
Command a trip and verify that the breaker opens but there is no reclose.
INHIBITION BY RECLOSING CONDITIONS
Close the breaker and wait for 5 seconds.
Command a trip, verify that the breaker opens and wait for the first shot.
Activate the inhibition input and command a new trip.
Verify that the breaker opens, wait for 8 seconds and verify that the relay does not reclose.
10.17.3 External reclose initiation
Close the breaker and wait for 5 seconds.
Activate the reclose initiation input and open the breaker, verify that the relay executes the first shot