CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES 4.1 ENERVISTA 650 SETUP SOFTWARE
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 4-31
4.1.8.4 Inputs/Outputs menu
The Inputs/Outputs menu includes all the inputs and outputs signals available in the device. Contact and virtual type.
(*) indicates online only, (**) indicates offline only
4.1.8.5 Records menu
The Records menu is only available in online mode and includes the possibility to retrieve all the records available in the
device. By serial or Ethernet.
(*) indicates online only, (**) indicates offline only
inputs/outputs
Contact Inputs Status of digital inputs in the Relay for each board according to the relay model.
Contact Output Status Status of digital outputs in the Relay for each board according to the relay model.
Contact Outputs
Operates
Status (activated or not) of the variables used to operate a contact output. To configure
these signals go to Setpoint > Relay Configuration > Outputs menu.
Contact Outputs
Resets
Status (activated or not) of the variables used to reset a contact output. To configure these
signals go to Setpoint > Relay Configuration > Outputs menu. This output reset
Command is only effective if latch is selected for Output Type setting on the I/O board,
thus the contact output has been configured to emulate function 86 (latching relay).
IO Board Status Status of I/O boards. This status provides if the hardware it is OK (boards matching relay
model, correctly inserted in their tracks, in good state and communicating through the
internal CAN bus).
Virtual Inputs Status of Virtual inputs latched (32) and self-reset (32).
Virtual Outputs Status of virtual outputs (configured in PLC Editor). Up to 512.
Remote Outputs States of remote outputs for IEC61850 models.
Remote Inputs Status of remote device and remote inputs for IEC61850 models.
Analog Inputs (*) Measurements coming from analog inputs (DCMA)
Virtual Output Latched Status of Virtual Output Latched (configured in PLC Editor). Up to 16.
Virtual output
Analogue
Status of Virtual OutputAnalogues configured in PLC Editor). Up to 49 float values and 49
integer values can be used.
Records (*)
Event recorder (*) Retrieval and visualization of snapshot event (all and new), control events and alarm panel.
By serial or Ethernet (ModBus RTU or TCP/IP)
Waveform capture (*) Retrieval of oscillography files, by Ethernet.
Fault Report (*) Retrieval and visualization of fault report files, by Ethernet.
Data logger (*) Retrieval and visualization of data logger files. Only by Ethernet.