CHAPTER 5: SETPOINTS 5.2 PRODUCT SETUP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-7
For this setting change to take effect, a reboot is required.
5.2.1.3 MODBUS protocol
ModBus Slave Addresses for serial and Ethernet communication and the ModBus port number used for ModBus TCP/IP. For
more detailed information go to appendix B in this manual.
5.2.1.4 DNP3 slave
Physical port, Slave Address for DNP, IP Addresses for Masters, TCP/UDP Port, Unsolicited Response parameters, Analog
scale factors and deadbands, message fragment size, Binary input block. For more detailed information go to appendix C
in this manual. DNP protocol is available for standard and IEC61850 models but it is not available Procome models.
Table 5-5: DNP protocol settings
Product Setup > Communication settings >ModBus ProtocoL
Name Default Value Step Range
ModBus Address COM1 254 1 [1 : 255]
ModBus Address COM2 254 1 [1 : 255]
ModBus Port Number 502 1 [0 : 65535]
Product Setup > Communication settings >DNP3 Slave
DNP3 Slave 1 > DNP3 Slave 2 > DNP3 Slave 3
Name Default Value Step Range
Physical Port NONE N/A [COM1:COM2:NETWORK]
Address 255 1 [0 : 65534]
IP Addr Client1 Oct1 0 1 [0 : 255]
IP Addr Client1 Oct2 0 1 [0 : 255]
IP Addr Client1 Oct3 0 1 [0 : 255]
IP Addr Client1 Oct4 0 1 [0 : 255]
IP Addr Client2 Oct1 0 1 [0 : 255]
IP Addr Client2 Oct2 0 1 [0 : 255]
IP Addr Client2 Oct3 0 1 [0 : 255]
IP Addr Client2 Oct4 0 1 [0 : 255]
IP Addr Client3 Oct1 0 1 [0 : 255]
IP Addr Client3 Oct2 0 1 [0 : 255]
IP Addr Client3 Oct3 0 1 [0 : 255]
IP Addr Client3 Oct4 0 1 [0 : 255]
IP Addr Client4 Oct1 0 1 [0 : 255]
IP Addr Client4 Oct2 0 1 [0 : 255]
IP Addr Client4 Oct3 0 1 [0 : 255]
IP Addr Client4 Oct4 0 1 [0 : 255]
IP Addr Client5 Oct1 0 1 [0 : 255]
IP Addr Client5 Oct2 0 1 [0 : 255]
IP Addr Client5 Oct3 0 1 [0 : 255]
IP Addr Client5 Oct4 0 1 [0 : 255]
TCP/UDP Port 20000 1 [0 : 65535]
Unsol Resp Function DISABLED N/A [DISABLED – ENABLED]
Unsol Resp TimeOut 5 1 [0 : 60]
Unsol Resp Max Ret 10 1 [0 : 255]
Unsol Resp Dest Adr 200 1 [0 : 65535]
Current Scale Factor 1 N/A [0.00001-0.0001-0.001-0.01-0.1-1-10-
100-1000]