7-6 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.1 IEC 61850 GENERIC SUBSTATION STATE EVENT (GSSE) CHAPTER 7: IEC 61850 PROTOCOL
7.1.5.2 UserSt bit pairs
Remote Outputs 1 to 64 originates GSSE messages to be transmitted to remote devices. Each digital point in the message
must be programmed to carry the state of a specific PLC operand. The UserSt (User Setpoint) setting is used to select the
operand which represents a specific UserSt function to be transmitted. These states are displayed in the F650 relay and in
the EnerVista 650 Setup software in the menu Actual Values > Input/Outputs > Remote Outputs > UserSt.
Each User Set point can only be programmed and displayed in EnerVista 650 Setup in the menu Setpoint > Relay
Configuration > Remote Outputs.
Figure 7-4: Remote outputs (UserSt)