CHAPTER 7: IEC 61850 PROTOCOL 7.2 IEC 61850 PROFILE FOR F650
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 7-201
7.2.7.3.12 PIXIT for 650 family of relays whose order code has Rear Ethernet Communication Board 2
option "H", "G", "K", "J", "L", "M" and IEC 61850 Edition 1
Reference documentation: PIXIT For F650 relay V1_10 firm7_52.
This document specifies the protocol implementation extra information for testing (PIXIT) of the IEC 61850 interface in:
F650 Bay Controller with firmware version 7.52
Together with the PICS and the MICS the PIXIT forms the basis for a conformance test according to IEC 61850-10. The PIXIT
entries contain information which is not available in the PICS, MICS, TICS documents or SCL file.
Each table specifies the PIXIT for applicable ACSI service model as structured in IEC 61850-10. The "Ed" column indicates if
the entry is applicable for IEC 61850 Edition 1 and/or Edition 2.
1 Pixit For Association Model
ID Ed Description Value / Clarification
As1 1 Maximum number of clients that can set-up an association
simultaneously
5
As2 1, 2 TCP_KEEPALIVE value. The recommended range is 1..20s
5 seconds but if no application message is
detected within the As3 value, the device
closes the connection.
As3 1, 2 Lost connection detection time
120 seconds (Configurable)
As4 - Authentication is not supported yet
As5 1, 2 What association parameters are necessary for successful
association
Transport selector Y
Session selector Y
Presentation selector Y
AP Title N
AE Qualifier N
As6 1, 2 If association parameters are necessary for association, describe
the correct values e.g.
Transport selector 0001
Session selector 0001
Presentation selector 00000001
AP Title NA
AE Qualifier NA
As7 1, 2 What is the maximum and minimum MMS PDU size Max MMS PDU size 120000
Min MMS PDU size 7000.
As8 1, 2 What is the maximum start up time after a power supply interrupt 90 seconds